I have a mobile home with a coleman evcon heat pump. I removed the top for cleaning and the condensor fan wires fell off before I could check their position. I have 3 wires, black red and tan. There is a small diagram on the motor to show where they go to, but I cant reference it to the blower. It looks like one terminal is marked grey, one black. I may have had them connected right ( I switched them around). I am not sure abot the fan operation. Is there a delay, does it kick on low, and high by temp or pressure. The unit was icing up and the blower seemed to slow down.  The return duct filter was trashed, so I replaced that. all I need to do is hook thr condensor fan up. Thanks for any help
 
 
Replies [ post reply ]
cplangelo@yahoo.com

junior member

7 post(s)
replied on 7/19/2007

RED GOES TO "COM" OR "C" ON THE DUAL CAPACITOR.
TAN GOES TO "FAN" ON THE DUAL CAPACITOR.
BLACK WILL BE CONNECTED ON THE DEFROST CONTROL BOARD.
THERE MAY BE A BLACK RELAY ON THE BOARD OR TERMINALS
MARKED "ODF1 OR ODF2". HOPE THIS HELPS. IF NOT E-MAIL ME BACK